Our factory now needs to install a transformer. During the installation, it was found that the resistance of the high-voltage side of the transformer to ground is 750 megohms, and the resistance of the low-voltage side to ground is 180 megohms. Can it be used? Why?
Reply #22009-03-13
What is the voltage level of the transformer? The high voltage cannot be less than 1 megohm per 1KV, and the low voltage cannot be less than 0.5 megohm. If the insulation does not meet the requirements and the transformer has been left for too long, you must first consider the oil to see if it is caused by moisture in the transformer. If possible, do various tests on the transformer, such as oil withstand voltage, chromatographic analysis, etc. Secondly, consider the internal problems of the transformer, whether there is insulation damage inside, or manufacturing issues from the manufacturer.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.