2009-03-15View Original

Thread Content

1) For motors that operate for short periods of time or in intermittent cycles, it is difficult to set the parameters when using traditional bimetallic switches; therefore, overload protection may not be necessary. Typical examples include various electric valves (some of which have built-in overload protection). (2) Motors with a rated power of not more than 3 KW that are not prone to overload may not be equipped with such a device. (3) Sudden power loss can cause greater damage to the motor than overload conditions; therefore, overload protection devices that are designed to cut off the main power supply should not be installed in motors such as fire pumps and fire fans.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.