Pipeline heat dissipation issue

2009-03-15View Original

Thread Content

I have a project that requires electric heating, but the process conditions are quite extreme; I’m turning to this forum for help. The basic parameters are as follows: stainless steel pipes with a diameter of DN80, and a minimum ambient temperature of -9°C. The minimum temperature that the material should be maintained at is 45°C, or 50°C (the heat dissipation calculated for the two different processing methods differs, and the temperature is set to reflect this difference). The insulation layer is 40 mm thick rock wool; that’s about all the details, right? If it’s not enough, leave a message; after all, I’m not an expert in craftsmanship. Those who know it would be great if they could explain the general calculation method: Please help calculate the heat dissipation under two temperature differences: loveliness: This post was last edited by ZJYSSF on 2009-3-21 at 18:58
Reply #22009-03-15
You can refer to SH 3010-2000, the Technical Specification for Insulation of Petrochemical Equipment and Piping; it contains methods for calculating heat loss after insulation. It should be available on forums, so you can search for it yourself
Reply #32009-03-15
Waiting online for the answer. . :'(Lift it up.) Don’t sink
Reply #42009-03-21
Electric heating as a solution isn’t really something that’s all that new, is it? I made a few of them many years ago. I checked recently; this calculation is usually carried out by the manufacturing process team. Of course, there are no specific regulatory requirements in this regard at present, so the methods used vary quite a bit. The common practice is to provide the relevant details to specialized manufacturers, who then help develop a solution. I’ve been waiting for samples from Wuxi Huaneng recently. I used to calculate it with the simple algorithm on it.
Reply #52009-06-04
The companies for calculation are as follows: 1. Temperature difference: 45 – (-9) = 54 degrees, which is approximately 55 degrees; 50 – (-9) = 59 degrees. Approximately 60 degrees; the insulation layer is rock wool with a thickness of 40 mm. The thermal insulation coefficient of rock wool is 1.163. The heat loss from a DN80 pipe is as follows: at a temperature difference of 55 degrees, it is 27.1 watts; at a temperature difference of 60 degrees, it is 29.6 watts. The actual heat loss from the pipe is: at a temperature difference of 55 degrees, 27.1 watts x 1.16 = 31.5 watts; at a temperature difference of 60 degrees, 29.6 watts x 1.16 = 34.3 watts. The power required for the electric heating tape is as follows: a self-regulating heating tape with a medium-temperature rating of 30 watts is used. The ratio between the heating tape and the pipe is 2:1, meaning that two meters of tape are wrapped around every 1 meter of pipe. Shanghai Haorui Electric Heating Equipment Co., Ltd., Liu Bin. Phone: 13817240224
Reply #62009-06-05
It exists in the principles of chemical engineering; a search should help to find a solution.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.