Is the safety barrier in a frozen state?

2009-03-15View Original

Thread Content

Our company uses P+F temperature safety gates of the KFD2-UT/UT2-EX1 type. Frequently, short-circuit alarms occur at some non-control points, and the red indicator light on the safety gate also flashes; the problem is resolved after replacing it with a new one. I’m not sure what’s causing this Please ask the experts to help solve this! ! ! !
Reply #22009-03-15
Firstly, I don’t understand why short-circuit alarms occur at some non-control points; under normal circumstances, it are the control points or interlocking points that experience temperature changes. The failure rate of safety barriers is indeed higher than that of the DCS channels. However, it is still recommended to check the external wiring for any short circuits, as well as for issues such as grounding or other types of interference. If this issue from the original poster occurs frequently, it should be a peripheral problem.
Reply #32009-03-17
Check the wiring; it’s most likely a wiring issue.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.