The instrument compensation wire is designed to be 1000 meters long, but 200 meters worth of it was purchased in 5 bundles. Can joints be used to connect these wires?
Reply #22009-03-18
It is generally not permitted. Since it has been purchased, it is recommended to weld it firmly in place and take proper protective measures. Use it for now; otherwise the boss will criticize us: lol
Reply #32009-03-18
The wires are all continuous from one end to the other; they can’t be connected in segments! I can’t understand what the person above said!
Reply #42009-03-18
I don’t think it will work; since there are connections in between, a part of it will be exposed to the outside, and thus the purpose of extending the cold junctions to a control room with a constant temperature won’t be achieved.
Reply #52009-03-18
May I ask the original poster: is the 1000-meter compensation cable used for connecting one thermocouple? If it’s about wiring a thermocouple, I agree with what was said above. If a junction box is added in between, it can still be used more or less. Five junction boxes need to be connected. If five thermocouples are wired, with 200 meters per one, then five bundles should be fine. It is recommended to check the drawings to see how the cable lengths are specified in the cable table.
Reply #62009-03-18
Theoretically, the signal will attenuate when the junction boxes are connected. If the requirements aren’t very strict, they can be soldered together with proper rain protection measures in place.:lol
Reply #72009-03-18
Compensation wires generally should not have intermediate joints (especially in newly installed systems); if joints are necessary, welding or crimping should be used, making sure that the positive and negative poles are not connected incorrectly.
Reply #82009-03-18
If the measurement requirements are not too strict, it can be connected and used
Reply #92009-03-18
It seems that there will be a significant error when connecting them. It depends on the situation in which the original poster plans to use them; if safety is a concern, it’s better to use them with caution

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.