There is a pipeline that originally had an electric butterfly valve with a DN100 size; now the diameter of this pipeline has been changed to DN150. I would like to ask whether it is possible to replace the DN100 butterfly valve with one of DN150 size, while continuing to use the existing electric actuator In other words, when the pipe diameter increases, the electric actuator remains unchanged; only the valve is replaced. Is it feasible?
Reply #22009-03-18
I think there’s enough drive for it; it depends on how strict you are about leaks. If not too strict, it should work fine, but if you’re strict, it’s better to replace them all together
Reply #32009-03-18
Check the water pressure; if it’s at normal pressure, that’s fine – perhaps the valve opens a bit slowly
Reply #42009-03-18
Well, the answer above is correct; the key factor is pressure. If the pressure is very high, your electric butterfly valve might burn out its small motor due to excessive load
Reply #52009-03-19
What was said upstairs is also correct! Pressure is very important! As the diameter increases, the torque required of the valve also increases. If an actuator that is too small is used, it will be difficult to operate the valve! :) Of course, some manufacturers produce valves with low torque; in such cases, you can use an actuator designed for a DN100 diameter! :) :) QQ: 928976489
Reply #62009-03-20
First, determine the opening torque of the DN150 valve (this value is provided in the valve manufacturer’s specifications, but it usually does not include a safety factor; this factor is not necessary to consider if the fluid is water). Next, find out the rated torque of the electric actuator and check whether it is greater than the valve’s opening torque. If it is, then the actuator can be used; otherwise, it is recommended to replace it. It is also necessary to verify that the flange on top of the valve matches the mounting flange of the actuator, otherwise installation will not be possible, and custom connectors will be required

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.