DeltaBar flow meter

2009-03-20View Original

Thread Content

In our plant’s dissolution workshop, DeltaBar flow meters are used to measure saturated steam, while the differential pressure transmitters are of the EJA110 type, with a range of 0–17.997 kPa. The flow rate at a differential pressure of 2.0 kPa is 30 t/h. For example, if I want the flow rate at 2.0 kPa to be between 20 and 23 t/h, what adjustments need to be made to the transmitters to achieve this? I hope Haiyou can help think it through!
Reply #22009-03-22
In differential pressure type flowmeters, the differential pressure value is calculated based on the size of the throttling element; the differential pressure value of the transmitter remains constant, and it is not possible to change the transmitter’s range without replacing the throttling element

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.