Valve hydraulic test

2009-03-20View Original

Thread Content

The pipeline installation of my methanol company has started, and the valves need to be pressure tested for leaks. Is there any relevant standard? Please give me some advice. Thank you very much! ! ! ! !
Reply #22009-03-20
GB/T13927-2008 http://www.414311.cn/BBS/frame.php?frameon=yes&referer=http%3A//www.414311.cn/BBS/thread-5164-1-1.html
Reply #32009-03-20
American standards generally use API598, the water pressure is generally 1.1 times the nominal pressure, and the air pressure is generally 0.6MPa.
Reply #42009-03-21
There is GB50235-97, the strength test pressure is 1.5 times the nominal pressure, and the tightness test is 1.0 times the nominal pressure.
Reply #52009-03-22
GB/T13927-2008 http://bbs.hcbbs.com/thread-421782-1-1.html
Reply #62009-03-22
It is best to check against the design drawings to see what specifications and standards are implemented. Key valves need to be supervised on site, because the quality of domestic valves varies greatly. In order to be responsible for the project, you are also responsible for yourself, so don't be lazy.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.