Is it necessary to install a flame arrester on the fuel pipeline before it enters the furnace?

2009-03-25View Original

Thread Content

This post was last edited by flute6 on 2010-9-16 00:24. Is it necessary to install flame arresters on the fuel pipelines before they enter the furnace? Do flame arresters get clogged easily?
Reply #22009-04-13
A flame arrester is necessary; regular cleaning will prevent it from getting clogged
Reply #32009-04-13
Since we mainly act as agents for imported flame arrestors, in a situation like yours it’s best to use a flame arrester. However, the gas may contain small solid particles; since our flame arrestors are quite small, around 1 inch in size, they can easily get clogged. It’s best to install a filter in front of them. If the diameter of the pipeline is large, then the flame arrestor can be cleaned regularly.
Reply #42009-05-05
Personal opinion: Fire arrestors must definitely be added, because if backflow occurs at the burner, the damage caused will be even greater!
Reply #52009-05-05
If it’s gas, I don’t think it’s necessary; a higher-level interlock system can be used. The pressure of gas is much higher than that in the furnace, so backflow basically won’t occur. Of course, a differential pressure interlock can be installed; when the differential pressure is low, the gas valve can be closed. Generally, gas valves are equipped with double-check valves. Of course, for safety reasons, the pressure difference value for interlocking can be set at a higher level
Reply #62009-05-06
Our situation is the same as what was mentioned upstairs: there is a low pressure interlock
Reply #72009-05-06
It is likely not necessary to install a flame arrester; generally, a on/off valve controlled by a solenoid valve is used to prevent the gas pressure from becoming too high or too low.
Reply #82010-09-15
The typical layout of the fuel gas pipeline before entering the furnace consists of a KV valve (controlled from the control room), a flow control valve (interlocked with the furnace temperature), and a flame arrester

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.