Has anyone ever set up boiler rapping in a DCS?

2009-03-27View Original

Thread Content

Set the rapping action in DCS: rap for one minute every 30 minutes, in 4 groups rotating in sequence, with three points per group; start manually and operate in automatic cycle. Is the vibrating action generally performed in a DCS, or is it controlled separately by a PLC? Let’s talk about it.
Reply #22009-03-28
With such a long time interval, there is no need for a PLC; a DCS will suffice.
Reply #32009-03-28
It’s best to have it in one system, as this makes maintenance simpler; whatever can be achieved with a PLC can also be achieved with a DCS
Reply #42009-03-28
You can operate it using DCS; once automatic operation is enabled, set the vibration time and the ash discharge time. For example, if the vibration time is 60 seconds and the ash discharge time is also 60 seconds, if you don’t want the vibration to last too long, you can set the time for the next action to 2400 seconds or more

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.