What is the actual air consumption when using switch valves and regulating valves?

2009-03-31View Original

Thread Content

When designing, the air consumption of the valve is generally calculated as 1-2NM3/H. In actual use, if the on-off valve does not operate, does it not consume air? How to calculate the air consumption for an on-off valve that does not operate frequently? What is the air consumption of a regulating valve equipped with the Yamatake positioner AVP-300?
Reply #22009-03-31
The factors considered are incomplete and are for reference only: The air consumption depends on the air supply pressure, switch stroke, volume and number of actions. It is calculated as follows: L/Min=Air volume (Air volume Opening + Air volume closing)××Action cycle times (/min) Liter/min = Cylinder volume (opening volume + closing volume) × × times/minute This post was last edited by zlky2005 at 2009-3-31 19:53 ]

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.