HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

Please tell me about the grounding problem of the 5000-liter oil tank farm.

2009-04-01View Original

Thread Content

Our company has a new oil tank farm. The size of the tank is 5000m3. Dear friends, how many grounding terminals should each tank have?
Reply #22009-04-01
Just place the tank in 2 places, one at each end. Assuming it's a vertical tank, I don't know the grounding location. Please help experts.
Reply #32009-04-01
I've only seen horizontal ones with one ground on each end. :)
Reply #42009-04-01
Horizontal ones generally have two places, and vertical ones generally have only one place, which can meet the grounding requirements. If the requirements cannot be met, you can consider adding a grounding electrode.
Reply #52009-04-01
This design meets lightning protection requirements. If the tank thickness is greater than 4mm, lightning rods are not required, but the grounding must be at least 2 points. . You need at least 2 points of grounding, at opposite ends of the diameter of the tank. .
Reply #62009-04-01
At least 2 points are grounded. The distance cannot be greater than 30m, otherwise it will be added. This is a relatively common method, but there is a problem. I wonder if you have noticed it. . For grounding such as oil tanks, you cannot just use the steel bars in the tank foundation. Regardless of whether the grounding resistance is sufficient or not, a ring grounding body must be installed 3 meters away. I have forgotten the specific reason. I have done this kind of design before, but then I checked the specifications and changed the design in the future ;P
Reply #72009-04-03
Irrigation areas are generally surrounded by annular grounding bodies, and the storage tank must be connected to the annular grounding body at least in two places.
Reply #82009-04-03
Thank you everyone above. I know the specific design, but I still want to know the specification number. If that sea friend knows the specification number, please let me know. Many thanks!
Reply #92009-04-03
Article 10.1.8 of "Technical Specifications for Electric Power Design of Production Equipment of Petrochemical Enterprises" SH3038-2000
Reply #102009-04-03
Go back upstairs: The content of Article 10.1.8 is: For high-rise metal structures, metal closed containers and pipelines with a wall thickness greater than 4mm (except oil tanks), air-termination devices do not need to be installed, but they should be grounded, and the grounding points should not be less than two. ; The distance between two grounding points should not be greater than 30m, and the impact grounding resistance should not be greater than 30Ω. It refers to lightning protection grounding and does not include oil tank areas, so it is not a correct answer. Hope to check.
Reply #112009-04-04
At least 2 places, with an interval of no more than 30m.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.