Experience in operating the device when it is restarted after being shut down

2009-04-03View Original

Thread Content

After the unit is restarted, since the conversion system is at the beginning of the entire process and involves many utility systems, desalinated water and steam are the first to be restored to operation. At this time, special attention should be paid to the liquid levels in the large and small steam drums, especially when taking readings. Both of these drum levels are equipped with interlocks; if these interlocks activate, it will cause the entire system to shut down. During this startup, I was occupied with taking readings that day, so I didn’t pay much attention to the liquid level in the large steam drum. By the time I noticed it, the liquid level in the drum had dropped below 20%, and the pressure had risen significantly. Due to the large fluctuations in drum pressure during the startup phase, the three-element automatic control system was not activated; moreover, the speed of the boiler feed pump was also low. Everything had to be adjusted manually. Therefore, the water supply flow rate was also below the interlock value due to the low pump speed and high drum pressure. Fortunately, that interlock was not activated at the time, and the issue was detected in a timely manner. By increasing the pump speed and opening PCV-13 to reduce the drum pressure, a serious accident such as a dry drum condition was avoided. In the future, during the startup phase, especially when taking readings, two people should coordinate with each other and must not be careless. During startup, as there are many people involved and the shift leader has a lot of tasks to handle, I need to pay even more attention to monitoring the liquid level promptly. Interlocked shutdowns or a dry drum in the steam drum must never occur.
Reply #22009-04-03
You’re absolutely right; we also experienced an extremely low level in the steam drum, and the control room could no longer display the liquid level. However, the on-site glass level gauge still indicated some liquid level present. At that time, the interlock system wasn’t activated, and the plant didn’t stop operating after making adjustments.
Reply #32009-04-03
It seems that everyone encounters chaotic situations while driving. While we were driving, the liquid level in the steam drum gave a low-level alarm; the steam drum was almost dry. This was because the main control system increased the load but did not raise the speed of the boiler feed pump to increase the water supply, which nearly led to an accident.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.