【Daily Question 20090405】Selection of air-operated control valves: air-open or air-close

2009-04-05View Original

Thread Content

Under which circumstances should a pneumatic control valve with a certain mode of operation be selected? ([ ) Open or Closed]): 1) The control valve at the compressor inlet should be of ( ) type. 2) The compressor bypass control valve should be of ( ) type. 3) For the compressor outlet pressure control system, when the control valve is installed on the vent line, the ( ) type should be selected. 4) The steam outlet control valve for the drum should be of ( ) type. 5) The drum feedwater control valve should be of the ( ) type with a right-mounted auxiliary positioner. 6) The control valve for the storage tank pressure regulation system should be of ( ) type. 7) For the storage tank level control system, when the control valve is installed on the inlet pipeline, the ( ) type should be selected. 8) For the storage tank level control system, when the control valve is installed on the outlet pipeline, the ( ) type should be selected. 9) For the fuel oil and gas system of the heating furnace, ( ) type should be selected. 10) For the feeding system of the heating furnace, ( ) type should be selected. 11) For the drainage line of the oil-water separator, ( ) type should be selected. 12) For pressure regulation of the container, if regulation is to be achieved by discharging material, ( ) type should be selected ; If adjustment is to be made using the incoming material, the ( ) formula should be selected. 13) For the outlet line of the distillation tower, the ( ) type should be selected. 14) For the reflux line of a distillation tower, the ( ) type should be selected. This post was last edited by Mobei Yihai on 2009-4-5 09:34.]
Reply #22009-04-05
There are too many questions; I’m afraid I won’t be able to answer them all. 1. Air-shutoff type, to prevent the tank from being collapsed due to excessively low pressure inside it in the event of a fault. 2. Air-controlled shut-off, 3. Air-controlled shut-off; vents open in case of failure, 4. Air-controlled shut-off; vents open in case of failure to prevent overpressure in the drum, 5. Air-controlled shut-off; opens in case of failure to prevent water shortage in the boiler, 6. This should also be related to the process pipelines; air-controlled shut-off for the outlet and air-controlled opening for the inlet, 7. Opens in case of air-controlled shut-off failure to maintain liquid level, 8. Closes in case of air-controlled opening failure, 9. Cuts off fuel in case of air-controlled opening failure, 10. Cuts off feed in case of air-controlled opening failure, 11. Air-controlled opening (uncertain), 12. Air-controlled shut-off, air-controlled opening, 13. Air-controlled shut-off, 14. Air-controlled opening. Last edited by chmyh on 2009-4-5 10:38.]
Reply #32009-04-05
1) The control valve at the compressor inlet should be of the (air-shut) type. 2) The compressor bypass control valve should be of the (air-operated shut-off) type. 3) For the compressor outlet pressure control system, when the control valve is installed on the vent line, a (air-operated shut-off) type should be selected. 4) The steam outlet control valve of the drum should be of the (air-operated shut-off) type. 5) The drum feedwater control valve should be a (air-operated) type with a right-mounted auxiliary positioner. 6) The control valve of the storage tank pressure regulation system should be of the (air-operated shut-off) type. 7) Storage tank level control system: when the control valve is installed on the inlet pipeline, a (air-operated) type should be selected. 8) Storage tank level control system: when the control valve is installed on the outlet pipeline, a (air-actuated) type should be selected. 9) The fuel oil system of the heating furnace should adopt a (air-operated) type. 10) The feeding system of the heating furnace should adopt a (air-shut) type. 11) For the drain line of the oil-water separator, a (air-actuated) type should be selected. 12) For pressure regulation of the container, if regulation is to be achieved by discharging material, a (air-controlled) type should be selected ; If adjustment is to be done using the incoming material, a (air-operated) type should be selected. 13) For the outlet line of the distillation tower, a (air-operated) type should be selected. 14) For the reflux line of the distillation tower, a (air-operated) type should be selected.
Reply #42009-04-05
1. Air shut-off, 2. Air shut-off, 3. Air shut-off, 4. Air shut-off, 5. Air shut-off, 6. Air shut-off, 7. Air shut-off, 8. Air open, 9. Air open, 10. Air open, 11. Air open, 12. Air shut-off/Air open, 13. Air shut-off, 14. Air open
Reply #52009-04-05
1) The control valve at the compressor inlet should be of the (air-shut) type. 2) The compressor bypass control valve should be of the (air-operated shut-off) type. 3) For the compressor outlet pressure control system, when the control valve is installed on the vent line, a (air-operated shut-off) type should be selected. 4) The steam outlet control valve of the drum should be of the (air-operated shut-off) type. 5) The drum feedwater control valve should be a (1-air-operated shut-off) type with a right-mounted auxiliary positioner. 6) The control valve of the storage tank pressure regulation system should be of the (air-operated shut-off) type. 7) Storage tank level control system: when the control valve is installed on the inlet pipeline, a (air-operated) type should be selected. 8) Storage tank level control system: when the control valve is installed on the outlet pipeline, a (air-operated) type should be selected. 9) The fuel oil system of the heating furnace should adopt a (air-operated) type. 10) The feeding system of the heating furnace should adopt a (air-operated) type. 11) For the drain line of the oil-water separator, a (air-actuated) type should be selected. 12) For pressure regulation of the container, if regulation is to be achieved by discharging material, a (air-controlled) type should be selected ; If adjustment is to be done using the incoming material, a (air-operated) type should be selected. 13) For the outlet line of the distillation tower, a (air-operated) type should be selected. 14) For the reflux line of the distillation tower, a (air-operated) type should be selected.
Reply #62009-04-05
1. Air-off 2. Air-off 3. Air-off 4. Air-off 5. Air-off 6. Air-on 7. Air-off 8. Air-on 9. Air-on 10. Air-on 11. Air-on 12. Air-off 13. Air-off 14. Air-on
Reply #72009-04-05
Each of the above answers has its own rationale, and they also reflect accumulated practical work experience; they should be quite comprehensive. However, one thing should be noted: these on/off conditions for the gas are not absolute; the process engineering team may have different requirements based on the characteristics of the process, and this is a situation that is often encountered in design work.
Reply #82009-04-05
1) The control valve at the compressor inlet should be of the (air-shut) type. 2) The compressor bypass control valve should be of the (air-operated shut-off) type. 3) For the compressor outlet pressure control system, when the control valve is installed on the vent line, a (air-operated shut-off) type should be selected. 4) The steam outlet control valve of the drum should be of the (air-operated shut-off) type. 5) The drum feedwater control valve should be a (air-operated) type with a right-mounted auxiliary positioner. ? 6) The control valve of the storage tank pressure regulation system should be of the (air-shut or air-open type, depending on the process requirements) type. 7) Storage tank level control system: when the control valve is installed on the inlet pipeline, a (air-operated) type should be selected. 8) Storage tank level control system: when the control valve is installed on the outlet pipeline, a (air-actuated) type should be selected. 9) The fuel oil system of the heating furnace should adopt a (air-operated) type. 10) The feeding system of the heating furnace should adopt a (air-operated) type. 11) For the drain line of the oil-water separator, a (air-actuated) type should be selected. 12) For pressure regulation of the container, if regulation is to be achieved by discharging material, a (air-controlled) type should be selected ; If adjustment is to be done using the incoming material, a (air-operated) type should be selected. 13) For the outlet line of the distillation tower, a (air-operated) type should be selected. 14) For the reflux line of the distillation tower, a (air-operated) type should be selected.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.