Station transformer

2009-04-06View Original

Thread Content

Is it necessary to have a station transformer at a 10KV substation? Is it possible to operate without one? If so, where can the power for the substation be obtained?
Reply #22009-04-08
Is this 10kV a substation or a switchyard?
Reply #32009-04-10
It is a switchyard, with power supplied directly via 10kV cables buried from the utility company’s 110kV station.
Reply #42009-04-10
Everyone believes a substation is needed. . Substations have low-voltage systems with low-voltage electricity, while switchyards do not have voltage transformation systems; only station transformers are available. This is just my personal opinion. Hehe
Reply #52009-04-10
Is it necessary to have a station transformer at a 10KV substation? Is it possible to operate without one? If so, where can the power for the substation be obtained? Answer: It is not necessary to have a station transformer; rather, a transformer is essential. Since it is a 10KV station, it should be a substation, with power supplied from a nearby high-voltage substation.
Reply #62009-04-10
What was said upstairs is correct; whether it’s a switching station or a substation, you need a power supply with a 400V voltage level. If there isn’t a transformer available nearby that can convert 10kV to 400V, then power has to be generated at another station for use in daily operations there, such as for the back-office equipment, lighting, and battery charging
Reply #72009-04-10
A transformer must be available in a 10KV substation. The station service transformer you mentioned likely refers to the transformer used specifically for control and protection functions in the substation; this can be determined based on the design requirements of your substation. It’s better to have such a transformer, or power can also be drawn from the 400V low-voltage side of the substation; it is recommended to include one.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.