Thread Content
The output of the differential pressure transmitter is 8 mA, but on the host computer, the value displayed by the card is half of the full scale. What could be the reasons for this?
The transmitter’s range does not match that of the lower-level device
Check the configuration issue to see if it’s a linear configuration
The square root operation was converted into a flow value. Last edited by ZZD109 on 2009-4-6 21:04.]
If the configuration and instrument settings are correct, such a problem will not occur.
It’s a configuration issue; the range settings for the lower-level device and the transmitter do not match.
1. The range of the master unit is half that of the transmitter, which may cause issues. 2. The square-root settings of the transmitter and the master unit do not match.
Check the configuration issue to see if it’s a linear configuration
Yes, it’s a problem with the range setting in the configuration
1. First, check whether the ranges of the primary and secondary measurements correspond; 2. Check whether the square root option is selected in the DCS configuration ; 3. Whether the DCS display references the value of another tag number ; 4. Locate the corresponding measurement point number on the DCS system terminal block, remove one wire, and use a multimeter to check whether the current is 8 mA. If it is, the issue lies in the DCS configuration; if not, the wiring and the primary meter need to be checked.