The catalytic unit measures pressure differences, reserves, pressure drops, etc., as well as the clearance of conduits

2009-04-07View Original

Thread Content

Those of us who have done instrument maintenance on catalytic units know that when there is blockage in the pipes used for measuring pressure differences, reserves, pressure drops, etc., it is a very troublesome issue. When the conduit is blocked, the instrument reading will be higher or lower (depending on whether it is the positive pressure side or the negative pressure side that is blocked). When the conduit is blocked, the catalyst can block the pressure-transmitting conduit of the reverse blowing air (which creates even more problems), or it can only block the primary valve, the vent valve, and certain sections of the conduit. When cleaning the ducts, we must be extremely careful and thorough; if a mistake is made, in mild cases this can lead to contamination due to the release of catalysts and contamination of the operator’s clothing, while in severe cases it can result in physical injuries and production accidents. I would like to ask those who have worked with catalytic units for any tips, advanced techniques, or sophisticated tools related to cleaning ducts. Often, when we give up, we artificially set a fake value for a single reading as a temporary solution; there’s nothing we can do about it. Especially when process technicians take catalyst samples, the excessive release of gas through the instrument vent valves is really frustrating; after all, they’re in charge and you can’t say anything to them. I would appreciate it if everyone could offer some suggestions – thank you very much.
Reply #22009-04-07
Connect the high-pressure nitrogen cylinder and use high-pressure gas to push.
Reply #32009-04-07
If it gets blocked, we often use an air blower directly, while vibrating the pressure transfer pipeline. If that doesn’t work, we’ll have to wait until the shutdown for maintenance.
Reply #42009-04-08
Hehe, if the blockage is severe, there’s no choice but to stop and carry out repairs!
Reply #52009-04-08
The problem of blockage in the pressure guide tube should be resolved at its root. Redraw the measurement pipeline for instruments: In accordance with HG/T20581-95 \"Manual for Automatic Control Installation\", if measuring gases, use the blowing method to connect the measurement pipeline ; If a liquid is being measured, use the flushing method to connect the measurement pipeline ; In accordance with HG/T20515-2000 \"Specifications for Chemical Process Automation Design\", in summary, the purging method can be used for measuring level, pressure, and flow rate in media that are corrosive, highly viscous, crystalline, molten, or sedimentary. In this way, the problem of blockage in the pressure guide tube is resolved.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.