Why must no loads be connected to either of the two-circuit power supply lines?

2009-04-11View Original

Thread Content

Recently, I was working on the issue of dual-circuit power supply, and the regulations state that no other loads should be connected to it. Why is this requirement?
Reply #22009-04-15
I work in relay protection. If branch loads are connected to a two-circuit system, the protection devices will not function properly, making it difficult to set their parameters.
Reply #32009-04-16
Loads powered by dual circuits are generally fire protection loads as well as Class I and Class II loads. To ensure the specificity of these loads (so that their operation is not affected by failures of other loads), it is not allowed to connect other loads to them.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.