There are currently eight S3-700 PLC cabinets, each equipped with one output module, 5 input modules, 35 safety barriers, and one 630VA transformer. The total circuit breaker rating for the entire system is 40A. Is this insufficient? What size circuit breaker is required?
Reply #22009-04-13
What is the power rating of a 630VA transformer? Does every cabinet have one of these? It’s that 40A bar. It’s best to calculate the power consumption of all the equipment in the cabinets, and then select a circuit breaker with a capacity that is about 20% higher than that value.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.