Is it necessary to connect a flammable and toxic gas alarm system to the DCS system?
Reply #22009-04-13
Generally, combustible and toxic gas alarm systems are installed separately
Reply #32009-04-14
If the combustible gas and toxic gas alarm systems you are referring to are installed independently, there is no need to connect them to the DCS system, as the independent gas alarm systems can fully meet the requirements for providing alarm alerts. However, if it is desired to see these alarms on the DCS system as well, then integrating it with the DCS system is an option; this is not a principle issue, and project owners often request this as well. If you want to introduce gas detection signals and alarm functions into a DCS system, it is important to ensure that the controllers, displays, and IO cards within that system are all configured independently. If there is a SIS system in that device, it is best to feed these signals into the SIS. However, one thing to note is that if the gas detection system has interlock signals, they cannot be fed into the DCS; either it must be set up independently or integrated into the SIS to carry out the interlock function.
Reply #42009-04-14
Actually, there is no need to introduce a DCS system, as alarm notifications can be handled through independent setups. Necessary interlock actions must be carried out whenever the levels of colored gases or toxic gases exceed the specified limits. If you want to incorporate gas detection signals and alarm functions into a DCS system, it is important to ensure that the controllers, displays, and IO cards in that system are all set up independently. If there is a SIS system in that device, it is best to feed these signals into the SIS. However, one thing to note is that if the gas detection system has interlock signals, they cannot be fed into the DCS; either it must be set up independently or integrated into the SIS to carry out the interlock function.
Reply #52009-04-14
The key is to check whether there is an SIS system; if not, it is better to introduce a DCS system for display and alarm functions. Our company has adopted DCS displays.
Reply #62009-04-14
Our company did not design the SIS system. The original design team’s approach was to create a separate system for flammable and toxic substances, to interlock it with the exhaust fans in each building, and to connect it to the DCS via communication lines for display purposes. Thank you all for your suggestions.
Reply #72009-04-14
There is no need to connect to a DCSS. The reasons are as follows: 1. Such devices operate as independent systems, with their alarm panels located in the control room. 2. If the purpose of connecting to a DCSS is for display and alarm functions, then it is unnecessary, as the audio and visual alerts provided by the alarm panels are much better than those of a DCSS. Moreover, connecting from the alarm panels to the DCSS would require additional cables and AI cards. 3. If the goal is to enable interlocking between certain components, this approach is also questionable. Consider the situation where detection probes are spread throughout the area to monitor concentrations of potentially hazardous gases, but the location of leaks is unknown – how can interlocking be achieved in such a case? Therefore, unless there is a direct causal relationship, interlocking seems unnecessary. 4. Even when connected to an ESD system and an emergency stop is triggered by a hazardous gas alarm, extreme caution should be exercised
Reply #82009-04-15
Refering to Article 3.0.10 of the \"Code for Detection and Alarm of Flammable and Toxic Gases in Petrochemical Enterprises\" SH3063-1999, the detection and alarm system for flammable and toxic gases should be a relatively independent instrumentation system. So it’s unnecessary; ordinary combustible gas detection alarms are usually interlocked with ventilation fans.
Reply #92009-04-19
In a few large projects I’ve worked on, both combustible gases and toxic gases were integrated into the DCS system for display. Maoming Petrochemical, Qingdao Refining & Chemical, Huizhou Refining & Chemical
Reply #102009-04-19
There is absolutely no need to create a comprehensive alarm system; one simple alarm is sufficient. When toxic or harmful gases are detected, a digital signal is sent to the DCS system to alert operators to which location there is an alarm, so they can check the gas monitoring system.:lol
Reply #112009-04-20
Introducing DCS facilitates operation by workers

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.