【Daily Question 20090415】What types of failures have occurred with thermal resistors in field use, and how were they addressed?

2009-04-14View Original

Thread Content

What types of failures have occurred with thermal resistors in field use, and how were they addressed? Format: Installation site: Fault symptoms: Cause of the fault: Solution: Pay attention to the posting format; original posts are encouraged. Spamming is not allowed. Original posts earn 10 points, while copied or spam posts result in a deduction of 10 points. This post was last edited by Mobei Yihai on 2009-4-14 20:59.]
Reply #22009-04-14
Installation site: Oil processing complex. Fault phenomenon: Unstable performance and poor reliability of the temperature sensing resistor. Cause of the fault: Improper installation of the sensor; the wires at its base were not fixed to the same steel structure as the sensor. Solution: Fix the wires at the base of the sensor to the same steel structure as the sensor
Reply #32009-04-15
Installation site: Heat exchanger for fermentation, equipped with two platinum resistance thermometers. Fault symptom: There is suddenly a large deviation in temperature. Cause of failure: There is a leak in the thermal resistor protective sleeve, allowing high-temperature material to enter at high temperatures. Solution: Fix the leakage.
Reply #42009-04-15
Installation site: Temperature sensing thermoresistors for the trays of the T-410 dehydration and refining tower. Fault phenomenon: The temperature difference between the 13th and 15th layers is more than 15°C. Cause of the fault: One of the thermoresistors is out of spec and needs to be replaced. Solution: When the temperature difference between adjacent layers exceeds 15°C, compare the temperatures of the layers above and below; remove the thermoresistor from the 13th layer, which has a lower temperature, send it for inspection, and replace it with a spare thermoresistor promptly.
Reply #52009-04-15
Installation site: Glue boiling tank for the preparation of papermaking auxiliary materials, with a single platinum resistance thermometer installed. Fault phenomenon: In the same area, there is a significant discrepancy between the readings obtained from platinum resistance thermometers and those from manual thermometers. Cause of failure: Poor thermal conductivity of the thermoresistor protective sleeve. Solution: Replace the thermoresistor protective sleeve

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.