The thermocouple is PT100; what is the model of the compensation wire?
Reply #22009-04-16
There are no thermocouples of the PT100 type; this is the calibration code for thermal resistors. No compensation wire is required – a regular cable will suffice.
Reply #32009-04-16
PT100 is a thermal resistor that does not require a compensation wire; a copper cable with a cross-sectional area of 1.5 square millimeters is sufficient
Reply #42009-04-16
PT100 is a thermal resistor, with 2, 3, or 4 wiring methods; the 3-wire and 4-wire systems employ compensation techniques. Users need to take no action; simply connect the signal cable.
Reply #52009-04-17
1. The fundamental differences among the three wiring methods for Pt100 platinum resistors: The two-wire and three-wire methods use the bridge method for measurement, and what is provided in the end is the relationship between the temperature value and the analog output value. The four-wire configuration does not use a bridge; it relies solely on a constant current source for sending current, with a voltmeter used for measurement, and the resulting value represents the resistance being measured. 2. The impact of the three wiring methods for Pt100 thermistors on measurement accuracy: The resistance of the connection wires and the contact resistance can have a significant effect on the temperature measurement accuracy of Pt100 platinum resistors. The three-wire or four-wire wiring methods for platinum resistors can effectively eliminate such effects. The detection devices connected to thermal resistors (temperature controllers, PLC inputs, etc.) all have four terminal connections: I+, I-, V+, V-. Among them, I+ and I- are used to provide a constant current to the thermistor, while V+ and V- are used to monitor the voltage changes of the thermistor in order to detect temperature changes. Please refer to the figure below: (1) The four-wire system involves connecting 4 wires to both ends of the thermal resistor; during wiring, the circuit loop and the voltage measurement loop are connected separately, which results in high measurement accuracy but requires more wires. (2) The three-wire system involves using three wires; when connecting a Pt100B platinum resistor, the reference point of the current circuit and the reference for the voltage measurement circuit are the same wire (that is, the I- terminal and V- terminal of the measuring device are shorted together). Slightly better precision. (3) In the two-wire system, only two wires are used; when connecting a Pt100B platinum resistor, the current circuit and the voltage measurement circuit are combined into one (that is, the I-terminal and V-terminal of the measuring device are shorted together, as are the I+ terminal and V+ terminal). The measurement accuracy is poor.
Reply #62009-05-06
Ah, this question is way too easy; any KVVVP cable with a 3*1.0 specification will do, and there’s no requirement regarding the cable model.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.