Thread Content
In petrochemical projects, the power demand of the wastewater treatment plant is around 1000 kW, which corresponds to multiple low-voltage electrical devices. Is it reasonable to supply power at low voltage from the main transformer, given that the distance is approximately 350 meters? If so, for such high power demands like 1000 kW, at what distance should high-voltage power supply be used? This post was last edited by xahoo on 2009-4-19 07:07
Your statement is too vague – is it one unit or multiple units totaling 1000 kW? 350 meters can also use low voltage if there are multiple motors that are not high-power
Supplying a 1000KW load with low-voltage power within a range of 350 meters is also cost-effective in terms of investment and operating expenses. It is also more economical to use only one 1000KW AC motor, powered by a low-voltage inverter of 690V!
Of course, a sewage treatment plant has multiple electrical loads; the poster is likely referring to the total low-voltage load of the plant being 1000 kW. Low-voltage power supply is also an option, but if the load is high and this results in the need for excessive amounts of cables, it is more reasonable to use a single transformer at the wastewater treatment plant.
Our experience: As an independent production unit, with a distance of over 200m and a load of over 1000KVA, it should be set up independently.
It is reasonable to use low voltage in such situations. The distance should mainly take into account the effect of voltage drop.
Wastewater treatment in factories is generally a separate unit; a 1000KW transformer should be installed