How to adjust the boiler water level gauge (double-chamber balancing vessel)?

2009-04-17View Original

Thread Content

How to adjust the boiler water level gauge (double-chamber balancing vessel with differential pressure transmitter)? What are the procedures for opening valves and draining sewage and what need to be paid attention to?
Reply #22009-04-18
This problem is more troublesome. When calibrating the transmitter, there is no pressure in the steam drum, and water is injected into the negative pressure chamber. The water cannot be filled completely because the density of water at room temperature is significantly different from the density of water under normal pressure in the steam drum. Therefore, when filling water, the height of the on-site water level gauge should be compared, and the static pressure should be matched with the range of the transmitter. Normally, every time the sewage is discharged, the transmitter must run to the maximum, and the negative pressure chamber must be filled with condensate water before it can work normally.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.