There’s no fire safety section, so I’m asking here

2009-04-19View Original

Thread Content

For the petrochemical project’s plant area, the fire-fighting water demand is 200 l/s. The calculated value for the fire-fighting water requirement in the tank areas is approximately 300 l/s (based on the maximum value); for other tank areas and auxiliary facilities, this figure does not exceed 100 l/s. In this case, one solution is to install two fire pumps with a capacity of 1080 m3/h each, one in operation and one as a backup; One solution: two units of 720 m3/h, one in operation and one as backup ; Is the flow rate of the fire pump set at its maximum value?
Reply #22009-04-21
In my opinion, fire pumps are not designed to operate at their maximum flow rate. As long as the maximum flow requirement can be met under accident conditions, that is sufficient. The solution proposed by the original poster should be the second one, as it allows for cost savings, and both pumps can be started simultaneously in the event of an accident. However, considering investment, floor space, and flexibility of use, a third option can be adopted: namely, two pumps with a capacity of 540 m3/h and one pump with a capacity of 300 m3/h. It is more flexible and energy-efficient to use.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.