I have been with the company for a long time. The company replaced the cooling water tower packing last year. Due to the non-standard construction at that time, a lot of original packing entered the system after the replacement. Currently, a lot of packing is blocked in the primary cooler pipe, affecting the heat exchange effect? Do you have any good ways to clean it up? The stuffing is from Sichuan, it looks like plastic.
Wash with large amounts of water or high pressure water
This post was last edited by Chuangxin Filling at 2009-8-6 09:40 and implemented according to the method above. What kind of plastic filler was used? If you can send me a picture, I can look at it. If you want to avoid blockage in the future, you can only change it again. This time, the construction is standardized and fixed with fixing devices and fillers.
3# We replaced the Chuangxin packing last year, but the supervisor did not do it properly, so...it won't work if there is water backwash.
Disassemble the primary cooler and the water blockage. If the water backflow is not thorough, you need to find a team to clean it with a high-pressure water gun. Pay attention to check other cooling equipment, fans, oil stations, couplers, air compressors, etc., and take precautions. Cleaning the pool is too troublesome.
You have no other option but to take it apart and clean it. Chemical cleaning doesn’t work, and washing it with water doesn’t work! High-pressure cleaning can’t be done without taking it apart! Do it slowly! Who told you not to pay attention to it?"