Thread Content
I would appreciate some advice from those who are more experienced: under what circumstances should a safety valve be installed on a tank? What kind of tanks require a vent valve and under what circumstances? And in some cases, just adding a vent is sufficient
If the material in the storage tank is not to come into contact with air, nitrogen protection is necessary; however, to avoid wasting nitrogen, the venting is minimal or non-existent. Therefore, both a positive pressure safety valve and a negative pressure safety valve must be installed to protect the storage tank.
Simply put, pressure-relief valves are installed on equipment operating at atmospheric pressure, while safety valves (burst disks) are used on equipment under pressure. In chemical plants, safety valves are installed on pressure vessels where the pressure exceeds 0.2 MPa to prevent overpressure. A breather valve is a ventilation device installed on fixed-roof tanks, which helps to reduce oil evaporation losses and control the pressure within the storage tank.
The 3rd floor is correct. Atmospheric pressure equipment handling flammable and explosive media should be equipped with a vent valve fitted with a flame arrester
Those who support the idea of a third floor need no further explanation!
3# Dr. Han, thank you for your valuable advice. Hehe, there are still a few points I’m not clear about: 1) A breathing valve is a ventilation device installed on fixed-roof tanks; it helps to reduce oil evaporation losses and control the pressure within the storage tank. ”Can bedroom containers and other types of tanks be equipped with breather valves? 2: For atmospheric pressure oil tanks, should breather valves or safety valves be used when the medium is relatively dangerous? 3: Does the breather valve only serve to balance the pressure inside the tank?
Vent valves are divided into flame-arresting vent valves and ordinary vent valves. The pressure range is generally from -295 Pa to +1570 Pa; they can be used for vertical and horizontal storage tanks, and help reduce losses due to the evaporation of raw materials during hot summer weather. Flame arrester: Primarily used on the vent pipes of Class A and B storage tanks to prevent external sparks from entering the tanks through those vent pipes
Safety valves are primarily used on pressure vessels; when the pressure inside the vessel reaches the designed level, the safety valve opens automatically to release the contents inside. When the pressure inside the vessel is below the threshold at which the safety valve opens, it closes automatically
According to safety assessments: When the pressure in a container exceeds its design pressure, or when the process involves an explosion risk, safety valves are necessary. Attention must also be paid to the flash point of the contents; if it is low, a flame arrester is also required
My question was actually highlighted, hehe. To summarize the answers from the experts: breathing valves are installed on equipment operating at atmospheric pressure, while safety valves (burst disks) are used on equipment under pressure. However, when the pressure in a container exceeds its design pressure, or when the process involves an explosion risk, safety valves are necessary. In chemical plants, safety valves are installed on pressure vessels with a pressure greater than 0.2 MPa to prevent overpressure. Attention should also be paid to the use of flame arrestors; for media in atmospheric-pressure tanks that are not hazardous, such as water tanks, only venting is required
This post was last edited by me108924 on 2009-9-4 08:57. What is the purpose of a breathing valve?.. In what situations is a breathing valve used?