Selection of cable conduit

2009-09-09View Original

Thread Content

I would like to ask experts: when choosing a conduit for the current ZRDJYPVP multi-core cable, 4x2x1.5, how should I make the selection? The coefficient required by the standard is 0.4. How to calculate it?
Reply #22009-09-09
For 4x2x1.5, a galvanized pipe with a diameter of 3/4 should be selected.
Reply #32009-09-09
A 3/4 pipe can’t accommodate 4×2×1.5, right? It doesn’t meet the standards and fails to achieve a coefficient of 0.4. I’ve seen that for 1×2×1.5 cables, 3/4” pipes are used for 1 cable per pipe, 1” pipes for 2–3 cables per pipe, 1-1/2” pipes for 4–6 cables per pipe, and 2” pipes for 7–15 cables per pipe. The 0.4 coefficient means that if the cross-sectional area of the conduit is 10, then it can accommodate cables with an area equal to 4 times that value; in fact, it’s normal to be able to fit 5 or 6 such cables as well.
Reply #42009-09-09
3/4 inch pipes are definitely too small; if the pipeline is long and has bends, it’s best to use 1-1/4" pipes
Reply #52011-11-26
Six In charge of will do just fine; there’s no problem at all

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.