May I ask who has requirements for DIICT4b explosion-proof wiring? Connect to armored thermoresistors, transmitter.
Reply #22009-09-19
It can be connected to an explosion-proof junction box, and the wiring method inside is very clear
Reply #32009-09-19
There are no special requirements for the wiring; make sure that the inlet is properly sealed.
Reply #42009-09-19
d Flameproof type II C for hydrogen; minimum ignition spark energy of 0.019 mJ. T4: safe object surface temperature ≤ 135°C. No special requirements for wiring, but due to the flameproof design, electrical connections (wiring terminals) must be properly sealed.
Reply #52009-09-19
Just make sure it is waterproof and dustproof; generally, explosion-proof hoses are used to connect the instruments, with interfaces that are usually M20*1.5
Reply #62009-09-20
5# cooldog_4412: You can refer to the HG28581 manual for automatic control installation. Generally, it is required that the electrical interface of the transmitter (usually 1/2NPT-F or M20*1.5-F) be connected using a gland seal; if it is an armored cable, it can be directly inserted into the cable tray. For unarmored cables, it is advisable to protect them with an explosion-proof flexible tube, and the same applies to platinum resistance thermometers.
Reply #72009-09-23
First, figure out the partitioning, and then consider whether it should be explosion-proof, increased safety type, intrinsically safe, encapsulated, and so on
Reply #82009-09-23
There are no particular requirements for the wiring in explosion-proof zones, but the sealing of the connectors must meet the same explosion-proof standards

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.