2009-10-22View Original

Thread Content

The heat tracing used in our factory does not have a water trap, nor does it have a water trap on the main pipe. I would like to ask if the resistance of the heat tracing is different depending on the length of the heat tracing. Some pipes may return water or steam, and if they are collected together, water hammer will occur.
Reply #22009-10-22
I have been engaged in production technology in the north for more than ten years. I have renovated and designed the heat tracing systems of two units in our factory. According to my experience, each heat tracing must have a water trap. First, it can avoid water hammer in the condensate line. Second, it can avoid shortcuts caused by steam and cause "short circuits." Third, it can avoid waste of steam resources.; In addition, attention should be paid to avoid "branching" of heating, "climbing" of heating for too long, and "sharp turns" of heating to prevent the heating from not being hot.
Reply #32009-10-22
Set up a water trap at a low position, otherwise it cannot be used even if water hammer safety is not considered, because the diameter of the heating pipe is usually very small and the steam path will be blocked by condensate.
Reply #42009-10-22
From the poster's introduction, the heat tracing used in your heating should be steam. As long as the trap is properly set up, water hammer will not occur.
Reply #52009-10-22
According to the specification, each heat tracing pipeline must be connected to a drain at the end.
Reply #62009-10-23
study* Old...thank you...I've also been looking at our company's drip pipe heat tracing recently...
Reply #72009-10-23
You can check it, SH_3126-2001 Design specifications for heat tracing and insulation of petrochemical instrumentation and pipelines
Reply #82009-10-23
A drain trap is a must. The operating status of each equipment is inconsistent, and it is best to have a water trap for each equipment. Together they will produce water hammer. We have been in a similar situation.
Reply #92009-10-24
Dear brothers, there are no drain traps now. I would like to ask you about the disadvantages and issues that should be paid attention to after using the drain trap besides waste.
Reply #102009-10-25
Personally, I think there should be. If the return water pipeline has a slope, it will inevitably accumulate water and hinder the passage of steam, unless the return water is discharged on site.
Reply #112009-10-25
You mentioned that in the heat tracing pipeline summary, you can consider using an automatic trap pump to transport the condensate to a designated location, which will reduce energy waste and the condensate can be reused.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.