2009-10-23View Original

Thread Content

1. The valves of the steam plate heat exchanger vibrate violently when opened. 2. When the control valve of one plate heat exchanger is opened, the pressure gauge on the steam distribution cylinder shows a pressure of 0.75 Mpa; when all five plate heat exchangers are open, the pressure drops to 0.2 Mpa.
Reply #22009-10-27
Based on the description, the large pressure difference before and after the system when multiple plate heat exchangers are in use is the cause of the vibration. If an automatic control valve is used for the valve ahead, it should be noted that such a control valve has specific requirements regarding the pressure difference between the upstream and downstream sides. Additionally, it is estimated that it is necessary to calculate whether the amount of steam supplied is sufficient.
Reply #32012-04-09
The steam must have condensed, that’s why the amount of steam is low
Reply #42018-12-13
The pressure difference between the front and back is too large; also, check whether there is enough steam supply

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.