Temperature control issue

2009-11-11View Original

Thread Content

I would like to ask an expert: For heating a reactor jacket with hot water, I need the temperature of the material inside to reach 70 degrees. The temperature of the circulating hot water is 90 degrees. However, there is no temperature measurement point inside the reactor. Is it possible to install a temperature sensor at the pipe where the hot water exits? Could it achieve good results? Is there any good way?
Reply #22009-11-11
Install temperature measurement points inside the reactor; otherwise, it’s impossible to accurately control the temperature of the material. What is the use of installing temperature measurement points on the hot water outlet pipe? I can’t quite tell
Reply #32009-11-11
First of all, I don’t know the size of your reactor; it is necessary to carry out calculations regarding the heat exchange requirements in order to determine whether heat tracing is feasible. Additionally, if you do not install temperature measurement points inside the reactor, it will be impossible to control the temperature, as heat tracing involves a heat transfer process. Since you don’t know the temperature of the material at the center of the reactor, it is best to add one or more temperature measurement points.
Reply #42009-11-11
It is recommended that you install a temperature sensing point on the reactor, so as to ensure accurate control of the temperature of the reactants. Otherwise, if a temperature measurement point is added at the outlet, the energy used for heat exchange cannot be calculated accurately; and as a result, even though it’s possible to control the temperatures of the hot water at the inlet and outlet, it’s still not possible to control the temperature of the reactor
Reply #52009-11-11
Adding temperature detection points by making cuts to the reactor vessel is rather troublesome, as after the pressure vessel leaves the factory, the user is not allowed to make arbitrary cuts in it; otherwise, the user shall bear full responsibility in case of any accidents. The best approach is to reasonably control the inlet temperature of the circulating hot water. The most appropriate inlet temperature for the circulating hot water in the reactor can be determined by considering the product specifications produced by the reactor; however, special attention must be paid to the impact of environmental temperatures during summer and winter on product quality.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.