Installation method for steam flow temperature and pressure compensation

2009-11-26View Original

Thread Content

Experts, please discuss how pressure and temperature measurement points should be installed in the temperature and pressure compensation for steam flow measurement Is the installation shown below correct? Temperature and pressure compensated steam flow meter; Schematic diagram of the temperature and pressure compensated steam flow meter: http://www.sensorok.com/newpic/XSJB.jpg
Reply #22009-11-26
The pressure should be applied in front of the flow meter, outside the straight pipe section.
Reply #32009-11-26
That’s right; the key is to ensure there is enough length of straight pipe section
Reply #42009-11-28
The effect of pressure on the flow meter is negligible. Regarding the normal process, the reason why the temperature and pressure measurement points are placed before the flow meter has not been clearly explained. I guess it might be because, after passing through the flow meter, there are still differences in temperature and pressure due to energy conversion and the actual conditions at the measurement section. But one problem is that, due to the installation requirements of the flow meter, the thermometer must be installed before the straight pipe requirement is met, and this piping installation poses difficulties.
Reply #52009-12-02
Pressure is in front, temperature is behind
Reply #62009-12-02
I prefer that the pressure and temperature measurement points be located before the flow meter, although I have also seen them placed after the flow meter.
Reply #72015-12-23
The pressure-taking element should be installed in front of the flow meter; installing it within a straight pipe section will not affect the flow meter’s measurement; The temperature sensing element should be installed behind the flow meter, at a distance of more than 5d; installing it in front of the flow meter will affect its measurement accuracy.
Reply #82015-12-29
Hehe, of course the pressure tap should be installed before the flow meter, because the orifice plate causes pressure loss. However, there’s nothing significant after measuring the steam system; the pressure loss across the orifice plate does not exceed 50 kPa, which is negligible compared to the steam pressure. The temperature doesn’t matter whether it’s high or low. The key is to leave enough straight pipe section.
Reply #92015-12-29
The standard installation is pressure in front of the gauge and temperature behind it!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.