What size current transformer is needed for 10,000 KW?

2009-11-30View Original

Thread Content

What size current transformer is needed for 10,000 KW?
Reply #22009-11-30
How can you calculate current without voltage? Without considering the current, how can one choose the transformation ratio? A motor of this size definitely isn’t 380V :sleepy:
Reply #32009-12-01
A motor of this size should operate at a supply voltage of 10 KV; for a motor with a power rating of 10,000 KW, a current transformer with a ratio of 1000/5/1 should be used.
Reply #42009-12-01
Incoming voltage of 10 kV, LZJC 10 200/5
Reply #52009-12-01
Based on the power you provided, the voltage required is estimated to be 10 KV. The power factor for ordinary motors, fans, and air compressors is 0.8; with this value, the current is around 700. Choosing 800 is a bit on the high side. You can use a setting of 100/5/1. As for the CT, whether to use 1000/5 or 1000/1 depends on the application scenario.
Reply #62009-12-04
The current transformer can be selected as 1200/5
Reply #72009-12-04
For a 10KV motor, the current is approximately 600A; in this case, a transformer with a rating of 800/5A will suffice, or a 1000/5A transformer can also be used. Such motors require winding differential protection, so it is not recommended to use transformers with a 1:1 ratio. For a 6KV motor, the current is around 1000A, and for this case, transformers with ratings of 1200/5A or 1500/5A can be used.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.