Doubts regarding the selection of the airtightness test pressure value

2009-12-03View Original

Thread Content

During the airtightness test of pipelines, the test pressure is the design pressure (with air as the medium), and it is required that all accessories be present. However, for the airtightness test of safety valves, the pressure used is 0.9 times the set pressure, and since this set pressure is less than or equal to the design pressure, the safety valve may activate during the airtightness test. How should such problems be resolved?
Reply #22009-12-03
The original poster didn’t consult the regulations; all that’s needed is to remove the safety valve and block it with a blind flange. The regulations clearly state that during pipeline pressure testing, the safety valve, rupture discs, as well as any instrumentation devices that cannot withstand pressure testing must be removed.
Reply #32012-04-12
The airtight pressure is generally 1.1 times the operating pressure. There’s no need to make it this high

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.