Hello, everyone! I have some questions regarding the design of the breathing valve on storage tanks: since the physical properties of the medium stored require a nitrogen seal, I wonder whether the nitrogen inlet should be connected directly to the inlet of the breathing valve, or whether it should have its own opening on the top of the tank. Also, I’m not sure about the location of this opening and its distance from the breathing valve. I hope experienced professionals can help me with this!
Reply #22009-12-05
They must be separated; the vent valve installed on equipment with a nitrogen seal should be a simple exhaust valve, designed to prevent excessive nitrogen seal pressure from damaging the storage tank.
Reply #32009-12-05
They can be separated using a ventilation cover along with a safety valve.
Reply #42009-12-06
I am looking for relevant information on this topic while studying*
Reply #52009-12-07
From a PROCESS perspective, is there any difference between installing the breath valve inlet separately? Basically, the amount of nitrogen that needs to be added should be the same.
Reply #62009-12-09
Could someone provide an authoritative answer? Those with practical experience, please. Thank you
Reply #72009-12-09
This post was last edited by Albertlu on 2009-12-9 at 18:11. Due to the relatively high pressure of nitrogen, a safety valve is required at the top of the tank (to prevent failures in the breathing valve and the automatic valve for supplying nitrogen). The maximum flow rate of nitrogen can be determined based on the tank’s maximum absorption capacity; the flow rate should be distributed evenly. Large tanks usually have several nitrogen supply openings, arranged symmetrically. Since the breathing valve serves as the passage for air in and out, a sensor and a nitrogen supply opening can be added near the breathing valve for safety reasons (they can be installed on either side of the breathing valve), as close as possible, in order to minimize air intake.
Reply #82009-12-10
I’m very grateful for the reply from above; it makes a lot of sense.
Reply #92009-12-11
Placing the nitrogen inlet close to the breather valve does not reduce air intake. Please think carefully. Under nitrogen sealing, the breather valve draws in air because the supply rate of nitrogen gas is not fast enough. Usually, when the liquid in the tank is pumped out, there is an insufficient supply of nitrogen, resulting in a vacuum inside the tank. If the tank is not designed to withstand a vacuum (which is often the case), and there is no breather valve to draw in air to fill the space, then it will be crushed by the external atmospheric pressure. The nitrogen supply rate depends on the diameter of the nitrogen pipe and the pressure difference, and is unrelated to the location of the nitrogen pipe connection. The location of the nitrogen inlet is typically determined with the aim of replacing as much of the residual air in the tank as possible with nitrogen (expelled through the breathing valve) when the tank is used for the first time or after being reused. From this perspective, the nitrogen inlet should be placed at a distance from the breathing valve, extending about 200 mm into the tank. For larger tanks, it is necessary to have multiple inlets distributed evenly, again with the aim of preventing short circuits caused by the nitrogen flow inside the tank and the formation of dead zones.
Reply #102009-12-12
This post was last edited by Albertlu on 2009-12-12 at 17:59. The gas needs to be distributed evenly so that nitrogen can be quickly supplied to the top of the tank. The pressure measurement points and supply points are determined based on factors such as the size of the tank’s top, the volume of exhaust gas, the size of the supply ports, and the nitrogen pressure. Usually, there are multiple points for measuring pressure and multiple ports for supplying gas. It is also sensible to include a nitrogen supply port near the vacuum breathing port; since the compensating gas is in flow, this allows for rapid pressure replenishment at the intake point, thereby reducing the amount of air drawn in. If there is only one nitrogen supply port and one vacuum breathing valve, the breathing valve should be installed in the center, near the top of the tank, while the pressure sensors and supply ports should be placed on either side of the vacuum breathing valve, which helps to minimize the amount of air drawn in. If the nitrogen supply port is located far away from the vacuum valve, more air will be drawn in. The area near the inlet of the vacuum valve is a critical point for both pressure measurement and gas supply; therefore, it is necessary to have supply ports and measurement points there.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.