This post was last edited by huchang417 on 2009-12-14 at 16:12. Hello everyone~ I have a question: can the filling factor of a buffer tank used for storing water be 1.0? What is the purpose of installing a safety valve on the top of a tank? Thank you all~
Fill with what water? The filling factor applies to liquefied gases; what is the purpose of a safety valve? Just read more about GB150 and you’ll understand.
2# baictq: I’ve learned about the concept of filling coefficient~ I’m a beginner~ Thank you for your guidance, dear Haiyou. Another question: can a buffer tank used to hold water be filled completely with water? One of the tanks here has a chilled water temperature sensor and a safety valve on its top – can the safety valve be used for draining water?
Safety valves also discharge liquid; generally, the top safety valve is installed to prevent excessive pressure in the gas phase space
If the filling coefficient of the buffer tank is 1.0, it will no longer be able to serve as a buffer. A value of 1.0 is acceptable for the time being, but if the tank remains full all the time, it won’t be very useful
5# qazxsw119 Oh, I have the same doubt. It has a temperature sensor on top; I think that if the liquid level doesn’t reach a certain level, then the sensor on top isn’t useful. What I’m trying to understand here is the classification system. According to the standards, if there’s no air space at the top, it’s considered non-standard; whereas if there is an air space and the conditions are met, then it falls into category one.