Estimation of the indicators for instrument consumption in the automatic control valves (including shut-off valves) of process units

2009-12-25View Original

Thread Content

I would like to ask my colleagues: what is the typical consumption of instrument air for automatic control valves (including shut-off valves) in process units? This value affects the capacity of the instrument air compression station.
Reply #22009-12-25
The specification is 2 Nm3/h, but in practice it’s not that much
Reply #32009-12-25
A control loop for a regulating valve consumes 1 Nm3/h of instrument air (purified air). I asked the instrumentation specialists in our department, and they all follow this approach: by counting the number of loops on the PID diagram, you can determine the total air consumption.
Reply #42009-12-26
2 Nm3/hr per control valve or KV (6 strokes)
Reply #52009-12-26
It is generally considered to be 4 Nm3/h per unit.
Reply #62009-12-27
It is generally considered to be 5 Nm3/h per unit.
Reply #72009-12-28
Among the answers provided by our enthusiastic friends, we have 1 Nm3/h, 2 Nm3/h, 4 Nm3/h, and 5 Nm3/h. Why are there so many different standards? Which one is correct?
Reply #82009-12-28
Grade 2 is relatively standard, but its usage in practice is very limited; if certain considerations come into play, it can be handled by using Grade 1, and there will be no major issues in practical applications
Reply #92010-01-06
According to the SH3020-2001 Design Code for Instrument Air Supply in Petrochemical Industries, the air consumption per control valve is taken as 1–2 Nm3/h. For the design capacity of the instrument air supply system, LZ is requested to refer to SH3020-2001 for calculations and design

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.