Regarding alternatives to lightning protection grounding

2010-01-10View Original

Thread Content

At our construction site, the structure of the compressed factory building is made of 0.6-thick color steel sheets; for lightning protection and grounding, brackets are installed on top of these color steel sheets, and then lightning protection wires are attached to them. Since the height of the compressed factory building is relatively high (26 meters) and the color steel sheets are thin, it is very dangerous for workers to work on that structure. We are now considering using the roof of the compressed factory building as a lightning strike conductor, in order to replace those wires. We wonder if this is possible. Could anyone among you please help us with this?
Reply #22010-01-10
According to Article 4.1.4 of the Code for Design of Lightning Protection of Buildings (GB50057-94), when there are flammable materials beneath a metal plate, its thickness shall not be less than 4 mm. In the design, it is likely that the compression plant is considered an explosion-hazardous area; since 0.6 mm is less than 4 mm, the lightning protection strip cannot be removed.
Reply #32010-05-05
Article 4.1.4 of the Code for Design of Lightning Protection of Buildings GB50057-1994(2000): Except for buildings classified as Category I lightning protection buildings, buildings with metal roofs should utilize their roofs as lightning receptors, and shall meet the following requirements: When overlapping is used between metal sheets, the overlap length shall not be less than 100 mm; II. When there are no flammable materials beneath the metal plate, its thickness should not be less than 0.5 mm ; III. When there are flammable materials beneath the metal plate, its thickness should be no less than 4 mm for iron plates, no less than 5 mm for copper plates, and no less than 7 mm for aluminum plates ; IV. The metal plate has no insulating coating. 0.6mm colored tiles can be used as lightning arresters if there are no flammable or explosive materials beneath them; however, there must be a good electrical connection between the tiles and the down conductors.
Reply #42018-04-26
Learn about real-world problems and get guidance from experts! Thank you!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.