What diameter can the tank outlet be equipped with or without a metal hose?
“It should be possible to determine the diameter of the tank outlet without installing a metal hose." You have to consider the role of the metal hose at the tank outlet.
The import and export of the tanks in our tank farm range from DN200 to DN350, all using metal hoses. However, for a chemical project in Shandong we worked on two years ago, we designed and used metal hoses, but the owner did not use them because they were too expensive. It has been used for two years now and there have been no problems. I think for the designer (conservatively) it is necessary to use metal hoses, and there must be foundation settlement of the storage tanks (we have four storage tanks in one unit in a tank farm, and only one tank has foundation settlement, and it is quite large 300mm). I suggest that the poster be more conservative.
The specification requires that metal hoses be added to the inlet and outlet of the storage tank, and the design must be done in accordance with the specification.
This post was last edited by lvshan2004-9 on 2010-1-25 20:25 1# fannyzhou "Oil Product Storage and Transportation Design Manual" Volume 1 P366 (23) The connection between the branch pipe in front of the tank and the main pipe should generally be flexible or elastic. When the intensity is greater than or equal to 7 degrees, the geology is soft, and the pipe diameter is greater than or equal to 150mm, a metal hose for anti-seismic storage tanks can be installed. The metal hose should be arranged between the first valve and the second valve close to the tank wall. …… According to this article, I do not install metal hoses if the inlet and outlet diameters are small, such as less than DN100. Please continue the discussion
Must be used, regulated: 1. Foundation settlement 2. Pipeline shrinkage 3. "Tips to the poster: Re-posting of content is prohibited and accounts will be banned" and other natural disasters. It's better to use it, otherwise it won't pass the review of the safety supervision department.
5# lvshan2004-9 This article only says that it can be set if it is greater than 150, but it does not say that it can be set if it is less than 150.
All should be set. The "Petroleum Depot Design Code" and "Petrochemical Enterprise Design Code" all require flexible connections in front of the tank. One is to consider tank settlement, and the other is seismic requirements.
This post was last edited by aymzj on 2010-1-19 14:57. Personal opinion: It is best to install them all, which can eliminate safety hazards and prevent accidents caused by settlement of the oil tank foundation! ! ! What the specification says must be mandatory. The owner can decide according to the material condition of the storage tank and the impact of the problem! ! For reference only! ! !
Generally, if it is less than or equal to 80, there is no need to install a hose.
personal opinion: There are two types of flexible connections: 1. Metal hose 2. Adjustable brackets. Whether metal hoses are needed can be determined based on the foundation. If the piling foundation or a small storage tank does not necessarily require metal hoses, adjustable brackets can be considered. I personally think it is unscientific to judge based on the diameter of the pipe. Feel free to comment.