This post was last edited by zhaohh3211 on 2010-7-28 at 15:38. I now have another relatively large project, and all the electrical equipment used in it is 0.55KW in capacity. But circuit breakers, contactors, thermal relays, etc. are still needed for control. The client requires the use of drawer cabinets; I am thinking of using 1/4 unit drawers. I wonder if anyone has used them before and whether they are safe. I’d like to offer some basic advice; thank you in advance, junior member.
This post was last edited by zhaohh3211 on 2010-7-28 at 15:39. A control box used on the device is acceptable.
This post was last edited by zhaohh3211 on 2010-7-28 at 15:41. I’m talking about the drawer cabinets of the MNS GCS GCK series!
This post was last edited by zhaohh3211 on 2010-7-28 15:43. No problem, after all, the power is low. It’s just that the space seems a bit small during maintenance.
This post was last edited by zhaohh3211 on 2010-7-28 at 15:44. It’s feasible; the power requirement is low, and circuit breakers, contactors, thermal relays, etc., take up little space. Additionally, a 1/2 unit drawer can be considered when combining the two.
It is possible as long as the drawer has sufficient capacity. However, if there are many components in the control circuit, it is recommended to use a single unit. Heat dissipation and maintenance must also be taken into consideration.
This post was last edited by zhaohh3211 on 2010-7-28 at 15:51. It’s possible; the power requirement is low, and devices such as circuit breakers, contactors, and thermal relays take up little space.
The 1/4 drawer cabinet is available only from ABB. I have visited ABB’s factory in Xiamen, where I saw that the material of the 1/4 drawers is plastic, and there is no partition between two adjacent drawers; therefore, if one drawer experiences a short circuit, it can easily affect other circuits as well. Therefore, I recommend avoiding its use as much as possible.
This post was last edited by zhaohh3211 on 2010-7-28 at 15:51. Thank you all for your comments; the manager insists on using 1/4 of a drawer, and there’s nothing I can do about it. I was wondering if anyone has encountered this situation before.
We have used them; generally, the maximum power of 1/2 unit is 7.5 KW, and it becomes unusable at higher levels. The components are difficult to assemble and maintain. In my experience, it’s best to use a single-unit drawer, but this increases the cost. It is possible to design combinations of drawers that include control circuits along with those that only provide power supply.
The power isn’t high, so there’s no problem; the largest we’ve made has handled 250A.