Since my major is not in the electrical field, I have the following question: Can RVV-3X2.5 cable be used as a power supply cable for 3kW systems?
Reply #22010-02-03
The RVV-3X2.5 cable can be used
Reply #32010-02-03
If your electrical load is a single-phase power load (220V), I think it’s a bit too small. It is recommended to use wires with a cross-sectional area of 4 square millimeters.
Reply #42010-02-03
What was said upstairs is correct; but if it’s for temporary use, it can still be used, though a safety factor of 4mm2 is required in that case.
Reply #52010-02-04
It can be used, but if the distance is too large, it is recommended to increase the wire diameter. .

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.