This post was last edited by sunjl1981 on 2013-1-6 at 21:17. The original design for the second phase of our plant called for 6 tanks, but only 4 tanks have been installed so far. During operation, PIC-216 experiences large fluctuations, which affects PIC-217 as well as the pressure before the hydrogen washing tower. After adjusting the PID parameters, the situation became more stable. Please share your thoughts – is this approach feasible? (After making the change, there are sometimes fluctuations even when the current is increased or decreased.) # hcbbs
Reply #22010-02-24
If other facilities such as pipelines are designed for six electrolyzers, then operation will not be as stable. At this point, the PID can be adjusted to regulate production and make it more stable.
Reply #32010-02-24
The PI parameters suitable for the hour regulator being inappropriate can lead to unstable pressure control. Generally speaking, it is impossible for the control parameters to achieve good control performance when the system load changes significantly. In addition to setting the parameters, attention must also be paid to the backflow control process of the hydrogen compressor to prevent interference between different components.
Reply #42010-02-24
The method we use for control now is to shut off the front vent, and reduce the backflow to a minimum – usually by opening 10–20 valve positions. When the rising and falling currents are relatively stable, fluctuations are less likely to occur. Does anyone have a better way to adjust it?
Reply #52010-02-24
During the driving phase, the hydrogen compressor pressure should be controlled manually. The control of the hydrogen main pipe pressure (hydrogen/chlorine pressure difference) should be automatic. It is better to use manual control for chlorine at this time, as differential pressure control is generally more stable. If it is unstable, modify the PI parameters.
Reply #62010-03-05
Is there a relationship between pressure difference fluctuations and potential blockages in bubble columns? Does the drying system affect pressure differential fluctuations? Please ask the experts to help solve it

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.