I am currently involved in the design and selection work for an LNG station at the institute. The compressor in the LNG station has a power rating of 11,500 kW; it is an 10 kV ABB synchronous motor, with a starting current of approximately 4.3 times its rated current. The power distribution system features one 35 kV incoming line, which is transformed via a 35/10 kV transformer. ABB recommends using LCI (soft start) to address system voltage drop issues. Our calculations show that an autotransformer can also meet 78% of the requirements for starting and system voltage drop. However, there are issues with the selection of the short-circuit reactance for autotransformers, and no relevant information is available on how to choose this value. I would appreciate your guidance on selecting the short-circuit reactance for autotransformers.
Reply #22010-04-12
Given such high power levels, it is recommended to use a soft starter. Starting with a reactor requires many more devices and takes up more space; although the cost is much lower, a soft starter only needs one switch cabinet (equivalent to the space of two cabinets). In contrast, a reactor-based system requires that much space, plus there are also a bypass circuit and a start switch cabinet, which adds to the complexity.
Reply #32010-04-12
2# Extremely attractive. Compared to the LCI method, only one additional side is added to the medium-voltage cabinet. The floor space required for an autotransformer is similar to that of an LCI (except that an oil-immersed type requires a separate transformer room); additionally, some LCIs need transformers of different voltage levels ; The cost is several million dollars lower after getting quotes.
Reply #42010-04-27
If a soft start method is used, feel free to contact me!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.