Condensing evaporator, cascade refrigeration, design, heat transfer temperature difference

2010-04-28View Original

Thread Content

This post was last edited by ZLF60137 on 2010-4-28 08:16: Condensing evaporator, cascade refrigeration, design, heat transfer temperature difference?
Reply #22012-04-13
I can’t see anything here! Is there no content? Solve!
Reply #32014-03-13
The design temperature difference for R22/R23 condensation-evaporation units is generally set at 5°C, while the heat transfer temperature difference for NH3/CO2 condensation-evaporation units is generally set at 3°C℃; The type can be shell-and-tube or plate heat exchanger; the latter is relatively more expensive, while the former requires a larger amount of refrigerant and a bigger expansion vessel.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.