Regarding the pressure rating of control valves

2010-05-16View Original

Thread Content

I would like to ask everyone: when selecting control valves and on-off valves, should the pressure rating be the same as that of the pipeline, or should it be one grade higher than the pipeline’s pressure rating?
Reply #22010-05-17
Agree with floors 2 and 3. Generally, the same grade is fine!
Reply #32010-05-18
The same grade will do. If the entire system has a small number of control valves, and there are only two pressure levels with the higher pressure level being more common, it is sometimes done for the sake of simplifying procurement orders and facilitating on-site installation by ordering the valves in the higher pressure category.
Reply #42010-05-18
The same rank is fine; that’s all I’ve seen.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.