2010-05-28View Original

Thread Content

A few days ago, I needed to service the heating pipes; when I opened the heating drain valve, I detected a gas smell. I lit it with a lighter. Where else in the methanol production system using coke oven gas could gas enter the low-pressure steam network?
Reply #22010-05-28
That’s so dangerous; the person who lit it must be really brave...
Reply #32010-05-28
Could it be that the upper pipe of the high-pressure water pipe inside the synthesis tower has cracked?
Reply #42010-05-28
I think I should first consider the source of the steam – whether it is the steam produced by the synthesis tower, or the combustible gases carried by the steam from the stripping tower Conduct non-condensable gas tests on the steam produced by each steam-generating device, and check them one by one.
Reply #52010-05-28
Thoroughly check which devices use gas and steam for heat exchange; it is likely that a leak in one of the heat exchangers used for gas and steam heat exchange is the cause. It’s too dangerous! ! ! ! !
Reply #62010-05-28
It’s also possible that it came from the water source! ! Both boiler water and deionized water exchange heat with the converted gas; it’s amazing what the original poster says – there’s a very strong coal smell! ! !
Reply #72021-02-12
Check the steam condensate for methanol and hydrogen sulfide in order to make a judgment
Reply #82021-02-15
Isn’t the factory area fire-proof? I guess you heard it from someone else too!
Reply #92021-02-25
Heating by water or steam? Check whether there is any leakage between the heat exchangers for gas, steam, or water

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.