Can a valve be installed at the inlet of the air cooler?

2010-06-02View Original

Thread Content

In actual production, I have never seen valves installed on the inlet and outlet pipelines of air coolers. However, if one of the groups in an air cooler starts to leak, it is impossible to carry out repairs without shutting down the system. I wonder whether it is possible to install valves during the design phase to isolate that particular group for repair purposes
Reply #22010-06-03
I don’t understand what the poster means by saying there is no valve at the inlet of the air cooler. The air-cooling inlets designed by our institute all come with valves.
Reply #32010-06-03
Some older units lack isolation valves at their air-cooling inlet and outlet connections when connected in parallel; as a result, if one of the air-cooling units fails or develops a leak, it cannot be isolated, forcing the plant to shut down for repairs. The design firm can be consulted to prepare revised designs that include isolation valves.
Reply #42010-06-03
We added valves. :):)
Reply #52010-06-04
From a design perspective, wherever shutdown is not necessary due to problems with the air cooler, an inlet isolation valve should be installed. Many of our company’s air coolers are equipped with such valves, and in many cases, given the winter temperatures, it is possible to bypass the air cooler and use direct feed lines instead.
Reply #62010-06-05
Our unit doesn’t have isolation valves, so it’s not possible to carry out maintenance at the moment; maintenance can only be done after shutting down the operation!
Reply #72010-06-05
The air-cooling inlet usually comes with a valve
Reply #82010-06-05
Don’t all air coolers have valves at their inlet and outlet? ? ? I don’t know what device is being referred to? ? ? First of all, cut-off valves should be installed at the inlets and outlets, and the reason for installing them is exactly as the original poster asked! ! ! Used for cutting.
Reply #92010-06-05
Our air cooler main pipe is not equipped with valves; valves are available at the inlets and outlets of the branch pipes, allowing them to be isolated for maintenance.
Reply #102010-06-06
We really don’t have any valves installed here, neither in the branch pipes nor in the main pipes; it’s very troublesome right now!
Reply #112010-06-06
Our air-cooled systems don’t have valves designed in them, but the company has required the design team to add valves, because without them it’s impossible to carry out maintenance

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.