Problems with the S7-300 AI module

2010-07-09View Original

Thread Content

I currently have an 8-channel AI module; 2 of the signals are of the 4-20MA type, while 6 signals are of the 0-20MA type. Initially, the negative terminals of those 6 0-20MA signals were connected to the negative terminal of 24, and everything was displayed correctly on the WINCC screen. Now, for some reason, the 2 4-20MA signals keep showing the maximum value
Reply #22010-07-09
First, verify the correctness of those two signals. Next, check for any sources of interference; for example, in the case of 4-wire signals, I short-circuit both the signal negative terminal and the power supply negative terminal. I’ll take another closer look
Reply #32010-07-09
Reply to 2# faner: All the signals are correct; everything is fine.
Reply #42010-07-09
1. Check whether the 24V voltage is normal. Then use a multimeter to check whether the current is greater than 20mA or less than 20mA. 2. There are spare parts; try another one. But it’s probably a wiring issue. 3. Check in STEP7 whether there are any fault messages for this module; if so, follow the instructions. 4. The usual connection method is to short-circuit Mama and M. From your description, it seems you have shorted M- (signal-) and M (power-). 5. Measure the voltage between M- and Mama. It feels like the high and low ends are connected together. Finally, call Siemens’ support line at 400-810-4288

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.