What is the safe distance in meters between the hydrogen production station and the nitric acid storage tank? This hydrogen production plant produces hydrogen via methanol conversion, and the nitric acid storage tank is an above-ground horizontal tank (50 m3)
Reply #22010-07-14
The hydrogen production station is classified as a Class A workshop, while the nitric acid storage tanks are classified as Class B storage tanks. According to Article 4.2.1 of the Building Code, it should be 12 meters plus 25%, which is 15 meters. If it is less than 25 meters, a fire separation distance of 25 meters shall be applied.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.